I went to look at a problem with a space heater causing a circuit to trip. After reviewing all of the loads on the circuit, it was found that 3 bedrooms and 2 baths had all been placed on a single 15-amp circuit, receptacles AND lighting.
I did the calc for amperage drawn by this small, oscillating space heater, which was labeled 1650 watts, which is 13.75 amps at 120V. In the same space was a clock radio, and a cordless toothbrush recharging stand. Figuring the heater is used only at night, so it being the only active load on the circuit, I wonder why a mfr would engineer a product so close to the threshold of max amperage for a common-sized household convenience outlet circuit? I could put a clamp-on ammeter on this and see what the actual draw is, but still it seems like the math indicates that I am close to the breaker threshold for tripping anyway, so a slight variation upwards in current would be a reasonable cause for the breaker to trip.
It's possible there's a weak breaker or some other unknown load plugged into the circuit. Does anyone have any knowledge on this kind of situation? Could it be in-rush current when the heater kicks on after the breaker has had time to warm up a bit after several cycles on-off-on? The breaker is in the garage and the outlet is probably 30 feet away. I have not changed the breaker yet, but right now am trying to sort out the best possible solution for the customer, given both baths are on this circuit as well (I have already suggested dedicating 20-amp circuits for the outlets at the basins).
Any advice is appreciated.
I did the calc for amperage drawn by this small, oscillating space heater, which was labeled 1650 watts, which is 13.75 amps at 120V. In the same space was a clock radio, and a cordless toothbrush recharging stand. Figuring the heater is used only at night, so it being the only active load on the circuit, I wonder why a mfr would engineer a product so close to the threshold of max amperage for a common-sized household convenience outlet circuit? I could put a clamp-on ammeter on this and see what the actual draw is, but still it seems like the math indicates that I am close to the breaker threshold for tripping anyway, so a slight variation upwards in current would be a reasonable cause for the breaker to trip.
It's possible there's a weak breaker or some other unknown load plugged into the circuit. Does anyone have any knowledge on this kind of situation? Could it be in-rush current when the heater kicks on after the breaker has had time to warm up a bit after several cycles on-off-on? The breaker is in the garage and the outlet is probably 30 feet away. I have not changed the breaker yet, but right now am trying to sort out the best possible solution for the customer, given both baths are on this circuit as well (I have already suggested dedicating 20-amp circuits for the outlets at the basins).