Any one see something wrong here
Sent from my iPhone using Tapatalk
Is till good to you?
Sent from my iPhone using Tapatalk
I was thinking the same.That looks like it is a manufactured listed package unit so the NEC wouldn't apply.
That looks like it is a manufactured listed package unit so the NEC wouldn't apply.
Any one see something wrong here
Sent from my iPhone using Tapatalk
Cannot see any grounding bonding for the equipment.
(there is a 4/o bear copper for lighting protection being use and is bounded to one column beam that has a ground about 200' away from that area)... A European company did all this not sure if they fallow NEC regulations.. also is there something for having a bear ground inside a metallic conduit with only white bushing at both ends
It is there if look closely there is a green conductor tie to the bare conductor on the upper side of the steel structure.. i think this is connected to the base of the equipment but not clealy visible in the picture..what would need bonding that isn't already?
there is probably an EGC of some sort feeding each motor.
quite possible there is one going into each box. the connection would likely be inside where it would not show in the picture.
there is no requirement that bonding conductors be external, or that the connections show up in pictures.