You cannot meet the NEC requirements by putting more rods but having them closer together. You would have to go to some different type of electrode.Thank you for reply, but if we have not enough spacing: can we install the rods with spacing 4.5 - 5 feet is it accepted?? but will not give us the required improving and we have to increase the nos. of rods to reach the required earth resistance , or we can not install rods with spacing not[?] less than 6 feet
we have a building and we have one side only available to install the rods, as per design we have to install 100 rods in area 76m x 3m (ROCK) to reach 2 ohm or less , then we have not any choice , the spacing will be 1.5m (4.9 feet) , , or we have to think about another solution by using PLATE/LATTICE ??
I cannot say for sure without getting the actual conductivity measurements, doing the calculations, and being a P.E. :angel:it is rock soil and we have to drill to install the rods and we have only 1 m backfilling by sand soil above the rock level, if we use plate/lattice it will be better than rods? and will give us improving
The first row of the rods must be away 1m from the building foundation. is that correct, please if correct ,refer to which NEC article no.?
I agree and would think if the EE asked for 100 rods that there probably was some effort involved in coming up with that figure. Once two rods have been installed, the rest are beyond the NEC requirements and there probably is more than six feet between at least two rods somewhere in those 100 rodsThe EE is requiring above & beyond NEC code. All direction with details should come from him. Your min requirement would stop at the 3rd rod based on the info given. at least 2 of the three would be 6' apart. a UFUR is stand alone GE and would not require a supplemental.