Hello
I went to a substation to check automatic transfer switch then I found that there is no distance between the terminal lugs for load and normal power sides. The contractor installed a rubber as insulation between the terminal lugs and I think it is not a listed rubber.
So can I use table 408.56 in NEC 2005 as a reference to determine the distance between terminal lugs?
Is the opposite polarity mean the different phases?
Your help is highly appreciated
I went to a substation to check automatic transfer switch then I found that there is no distance between the terminal lugs for load and normal power sides. The contractor installed a rubber as insulation between the terminal lugs and I think it is not a listed rubber.
So can I use table 408.56 in NEC 2005 as a reference to determine the distance between terminal lugs?
Is the opposite polarity mean the different phases?
Your help is highly appreciated