spacing on a pole line

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
Where would I find requirements for spacing between 5KV, a second 5kV 3 phase line and then 120/240 and below that telephone.

The 5kV are both Hendrix so I suppose they would be helpful where that is concerned. But what code defines this stuff.

Thanks,

Mike
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I agree with rick5280. See NESC-IEEE C2 the last edition[2017].
In my opinion this rule would be relevant[on my 2007 edition:ashamed1:]:
Rule 235???. Clearance for wires, conductors, or cables carried on the same supporting structure.
 

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
Also note this may get into PSC regulation of pole use. Google up "one-touch, make-ready" for some insight into the turf battle for pole space in places Google Fiber is deploying.
 