spas
does the the outdoor spa code apply when installed inside a pool house w/ pool,bar,sauna,etc..as far as disconnecting means
Re: spas
Why wouldn't it?
Some aspects may differ, such as any 3R enclosures, but the intent would remain the same.
Re: spas
No, that's not correct.
680.42 is called "Outdoor Installations."
680.43 is called "Indoor Installations."
If a hot tub is installed inside, you do not need to comply with sections dealing with "Outdoor Installations." It's not outdoors. It doesn't apply.
NEC-2005 680.43 Indoor Installations. A spa or hot tub installed indoors shall comply with the provisions of Parts I and II of this article except as modified by this section and shall be connected by the wiring methods of Chapter 3.
Re: spas
Originally posted by kevinnye20:
does the the outdoor spa code apply when installed inside.....as far as disconnecting means
Originally posted by celtic:
Why wouldn't it?
Some aspects may differ....
Are you sure?
680.12 Maintenance Disconnecting Means.
..... shall be accessible and within sight from its equipment.
Re: spas
680.12 is in Part I.
680.42 is not. :D
Re: spas
The way this question is ask the only answer that could be given would be yes. The wiring method would be different but the disconnecting means would be the same no matter where it was installed.