• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

SPD - Breaker Location

Merry Christmas

Keri_WW

Senior Member
Question: For a type 2 SPD that is protecting a switchboard, does it matter where in the lineup it is installed?

Details: I have had to take over a project in construction for an engineer that has left the company. He rejected the first switchboard submittal stating that the SPD needed to be in breaker position 1. The manufacturer says this is not possible since the bussing is offset for bigger breakers first. I don't think it matters where the SPD is installed, but wanted to see if there was a legitimate reason for location.

Thanks,
Keri
 

Keri_WW

Senior Member
Only documentation I can find states < 10-ft from SPD to bus; nothing about positioning in the gear. I am trying to reach out to their engineering department, but I don't really see it making a difference.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Only documentation I can find states < 10-ft from SPD to bus; nothing about positioning in the gear. I am trying to reach out to their engineering department, but I don't really see it making a difference.
It makes no difference what position it is in.
It is probable the switchboard manufacture has more experience installing SPDs than the other engineer had.
 
Top