I'm looking to install some surge protection for a quasi-industrial site with several CNC-type machines, robots, etc. The service is 480V - Y. There is (as required) the neutral at the outside service disconnect. From there, only the three phase conductors and ground go several hundred feet inside the building to the breaker panel. Would it be better to install a SPD at the service disconnect and use a 4-wire device or at the inside panel with only 3 wires(+gnd)?
It seems like outside would have a better path to divert surges, but I believe it's typically recommended to install SPDs closer to the equipment it's intended to protect.
Also, if I put the SPD at the panel with no neutral, would it matter that the device is labeled as being for a delta system? It seems like most 3-wire devices are so labeled (being a more common occurrence).
Finally, the service disconnect is a fused switch and the breaker panel is full. Though I know it's not kosher, I'm tempted to 'double-tap' the SPD wires onto a breaker or the switch lugs. Are there better/more approved methods?
Thanks as always.
It seems like outside would have a better path to divert surges, but I believe it's typically recommended to install SPDs closer to the equipment it's intended to protect.
Also, if I put the SPD at the panel with no neutral, would it matter that the device is labeled as being for a delta system? It seems like most 3-wire devices are so labeled (being a more common occurrence).
Finally, the service disconnect is a fused switch and the breaker panel is full. Though I know it's not kosher, I'm tempted to 'double-tap' the SPD wires onto a breaker or the switch lugs. Are there better/more approved methods?
Thanks as always.