SPD Required on RV Pedestal

B677

Member
Location
Florida
Occupation
EC
Running a new conduit and 1/0 feed to metered earth buried pedestal GE1LM532ES

Inspector dropped requirement for GFCI but wants SPD. This pedestal likely does not allow double tapping the lugs for a type 1 SPD. Looks like it only has one double pole breaker slot open.

Looking for ideas to install a SPD.

Thoughts:
  • Remove single pole 20A and replace with double pole 20A
    • One leg of SPD to breaker
    • Other leg pigtailed Breaker to Receptacle hot and other leg of SPD
    • Never done this but technically both poles of the breaker are in use; is it code?
  • Polaris with 3 ports
    • not sure there will be wire to use these on in the customer side of the RV panel
Anyone have any good ideas?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
RVs are full of electronics. Most owners have their own SPDs. I am pretty sure the SPD requirement is for dwelling units
 