Running a new conduit and 1/0 feed to metered earth buried pedestal GE1LM532ES
Inspector dropped requirement for GFCI but wants SPD. This pedestal likely does not allow double tapping the lugs for a type 1 SPD. Looks like it only has one double pole breaker slot open.
Looking for ideas to install a SPD.
Thoughts:
Inspector dropped requirement for GFCI but wants SPD. This pedestal likely does not allow double tapping the lugs for a type 1 SPD. Looks like it only has one double pole breaker slot open.
Looking for ideas to install a SPD.
Thoughts:
- Remove single pole 20A and replace with double pole 20A
- One leg of SPD to breaker
- Other leg pigtailed Breaker to Receptacle hot and other leg of SPD
- Never done this but technically both poles of the breaker are in use; is it code?
- Polaris with 3 ports
- not sure there will be wire to use these on in the customer side of the RV panel