How to size a SPD. We have a 600a 120240 single phase service disconnect that's need a SPD. Would a 50ka rated SPD work? Sqd # HEPD50
 
Any SPD with leads may work…some SPDs require OCPD ahead of the device, those are likely type 2. A type 1 may be ok but you need to see if you can tap the load side wires.
And with SPDs you get what you pay for and more is better, said Mike Holt once
Might be easier to install on a downstream panel and then point of use at electronics which is everything these days
 
Sizing depends on what you are trying to suppress.
In Florida the amount of lightning usually warrants more than a 50kA unit. Multiple levels of protection are suggested.

In other parts of the country, like Wisconsin, lightning is not as likely so 50kA units at the main, with occasional point of use devices, are typical.
 