I've got a couple of questions regarding surge protection devices (SPDs). Just when it seems that I have a firm grasp of the actual functionality and limits of SPDs, someone writes a white paper or article throwing another wrench in my already tooled-up brain.
I was relieved when I ordered Mike Holt's CD on Grounding vs. Bonding and he basically affirmed what I believed to be true when he said that he didn't understand all the hubbub the SPD industry makes when it insists that an effective ground be present in ones system for a home SPD to work effectively. He said that a SPD basically shunts the surge to the neutral thus making the ground of little consequence. Then I read the IEEE paper on lightning and SPDs where they state:
2.3.1 Grounding
"An effective, low-impedance ground path is critical for the successful operation of
an SPD. High surge currents impinging on a power distribution system having a
relatively high grounding resistance can create enormous ground potential rises
(see Section 4 beginning on page 30), resulting in damage. Therefore, an
evaluation of the service entrance grounding system at the time of the SPD
installation is very important."
As an aside, I overheard two electricians arguing about one of their home PCs being connected to a SPD. Evidently, one of them had an SPD hooked up between his home receptacle and his PC but his buddy had noticed that the ground indication light on the SPD was not illuminated, indicating that there was not an effective ground either at that receptacle or possibly in his entire house. The guy whose PC was hooked up to the SPD shrugged it off saying that he had a UPS plugged into the SPD which, even if the SPD were to fail, the UPS batteries would absorb any surge---Hmmmmmmmmm.
Man-O-man, would I appreciate a little clarity on this topic.
Dan
I was relieved when I ordered Mike Holt's CD on Grounding vs. Bonding and he basically affirmed what I believed to be true when he said that he didn't understand all the hubbub the SPD industry makes when it insists that an effective ground be present in ones system for a home SPD to work effectively. He said that a SPD basically shunts the surge to the neutral thus making the ground of little consequence. Then I read the IEEE paper on lightning and SPDs where they state:
2.3.1 Grounding
"An effective, low-impedance ground path is critical for the successful operation of
an SPD. High surge currents impinging on a power distribution system having a
relatively high grounding resistance can create enormous ground potential rises
(see Section 4 beginning on page 30), resulting in damage. Therefore, an
evaluation of the service entrance grounding system at the time of the SPD
installation is very important."
As an aside, I overheard two electricians arguing about one of their home PCs being connected to a SPD. Evidently, one of them had an SPD hooked up between his home receptacle and his PC but his buddy had noticed that the ground indication light on the SPD was not illuminated, indicating that there was not an effective ground either at that receptacle or possibly in his entire house. The guy whose PC was hooked up to the SPD shrugged it off saying that he had a UPS plugged into the SPD which, even if the SPD were to fail, the UPS batteries would absorb any surge---Hmmmmmmmmm.
Man-O-man, would I appreciate a little clarity on this topic.
Dan