Doc13067
Senior Member
- Location
- Bucks County/Philadelphia, PA USA
We are on the 2017 NEC so surge protection is not a requirement in my state. But because of recent surge issues with mini splits, I am trying to get all of my clients surge protected. I am unfortunately a Generac dealer so a few of my clients have transfer switches as the main service disconnect. So if I were to put a main breaker panel mounted SPD in what used to be the main panel it would exclude the ATS and generator upstream of it. So I am looking at how to get the SPD in the ATS or meter socket. I am thinking of removing lug mount nuts and putting eyelet crimp connectors on the posts under the nuts either in a meter socket or on the bars in the ATS. Just out of curiosity do any of you have a method for getting surge protection in front of a resi auto standby generator? For those of you who have to put outside main disco if you only had a main breaker enclosure with no additional spaces, you would be faced with the same issue. I don’t want to double the SPD wires with the service or feeder wires. I see no value in putting number 12s next to 4/0 under the same lug.
I asked about something like this once before and I got some bot telling me to “stop! and call an electrician!” and giving me a classroom lecture about how these things work lol remember that?