N new_ee Senior Member Mar 22, 2006 #1 Would these be covered in the NEC? Where? Specifically, whether they need to be plenum rated or not in a dwelling unit?
Would these be covered in the NEC? Where? Specifically, whether they need to be plenum rated or not in a dwelling unit?
ryan_618 Senior Member Location Salt Lake City, Utah Mar 22, 2006 #2 Article 640. They don't need to be plenum rated, unless you are installing them in "other space for environmental air", which is unlikely.
Article 640. They don't need to be plenum rated, unless you are installing them in "other space for environmental air", which is unlikely.
N new_ee Senior Member Mar 22, 2006 #3 Actually, they are being installed in the area above the ceiling so I think they might need to be plenum rated.
Actually, they are being installed in the area above the ceiling so I think they might need to be plenum rated.
ryan_618 Senior Member Location Salt Lake City, Utah Mar 22, 2006 #4 Just becasue they are above a ceiling doesn't mean they are in an air handling space. I have never seen a plenum ceiling in a dwelling. Is there NM cable above the ceiling? If so, that would be a violation if it is an air handling space.
Just becasue they are above a ceiling doesn't mean they are in an air handling space. I have never seen a plenum ceiling in a dwelling. Is there NM cable above the ceiling? If so, that would be a violation if it is an air handling space.
N new_ee Senior Member Mar 22, 2006 #5 You're abosolutely correct. Theres no air handling going on in this ceiling space and plenum rated cable will not be required.
You're abosolutely correct. Theres no air handling going on in this ceiling space and plenum rated cable will not be required.
S shortcircuit2 Senior Member Location South of Bawstin Mar 23, 2006 #6 new_ee Any speaker wiring in that dwelling must be listed for the purpose according to 725.82 shortcircuit2
new_ee Any speaker wiring in that dwelling must be listed for the purpose according to 725.82 shortcircuit2