My spec book requires me to do a coordination and arc flash study in accordance with "redbook standard 141" based on equipment supplied.This is a school and if I'm not mistaken "141" is for industrial facilities,in addition I'm at 3rd level protection (4000 amp fuse feeding fusible switchboard with 200amp to 800amp fuses in turn feeding my panels).What standard if not 141 should I be basing my study on?BTW all equipment is 208v.