Spec Requirement

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Came across this in spec.

"essential emergency circuits (Life safety and Critical in rigid conduit) or luminaire in circuit."

Is Life Safety and Critical circuits defined and clear in the NEC?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What type of facility is the area/building ??'
If it's healthcare:
517.19 is Critical Area, 517 Parr III is Essential.

That requirement sounds more like a critical operations area. If so:
If it's a "Critical Operation Center", then Art 708 specifically 708.10
 
Last edited:

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
What type of facility is the area/building ??'
If it's healthcare:
517.19 is Critical Area, 517 Parr III is Essential.

That requirement sounds more like a critical operations area. If so:
If it's a "Critical Operation Center", then Art 708 specifically 708.10
Healthcare. Ty
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I know of one large hospital that requires RMC and IMC for Critical and Life Safety feeders and has it written into all their new construction and renovation specs.

It does not apply to branch circuits though.
 