Which do you see specified more for receptacles 15A or 20A?

I see 15A rarely as most of the specs seem to ask for 20A rating.
 
On commercial it's always spec'd 20 amp duplex receptacles. Dumb but I think that many designers don't know that a 15 amp duplex is permitted on a 20 amp circuit.
Back when I sold receptacles, I had one contractor that would buy a cheap residential brand because its face looked like the more expensive spec'd style. I would not put it past him to use the <$1 ones if 15A were allowed.
 
I would not put it past him to use the <$1 ones if 15A were allowed.
I agree that some contractors will cut that corner if they can get away with it. As with anything that is part of a specification someone needs to check for compliance.
 
So are you saying that (1) 15a duplex can be put on a 20a circuit?
Yes if there is more than one receptacle on a 20 amp each receptacle can be 15 amps. One 15 amp duplex would be permitted to be the only receptacles on the 20 amps circuit.
 
So are you saying that (1) 15a duplex can be put on a 20a circuit?
Yeppers. This must match the circuit:

1696871923887.jpeg

By the way, a 15a receptacle is able to carry 20a; the difference is the slot shape.

For a given grade of receptacle, the internal parts are the same metal and gauge.

 
Yeppers. This must match the circuit
I would say that it doesn't need to match the circuit OCPD it needs to be equal or greater than the OCPD/circuit size. The 20 amp single device in the photo is permitted on a 15 amp circuit. :)
 
Yes if there is more than one receptacle on a 20 amp each receptacle can be 15 amps. One 15 amp duplex would be permitted to be the only receptacles on the 20 amps circuit.
I was always taught that because a duplex receptacle is under one yoke that it is considered one device and one 15A duplex cannot be put on a 20 amp circuit.
 