paullmullen
- Wisconsin
- Electrical Engineer & Master Electrician
Because of the differences between start-up current and running current in motor circuits, it is common for the conductors to to be differently sized than might be implied by using T310.15(bB)(16) alone. A DIYer or other person following behind me might look at the 70A circuit breaker for the heat pump I'm installing and think... "oh cool, the conductors are sized for 70A" without actually checking to see that they're actually 8AWG THHN. They might just think "Ah, 70A breaker, that must be appropriate for a 70A continuous load" and misuse those conductors during a remodeling.
So here's my question: Do any of you mark motor circuits at the breaker panel in a special way to ensure that future modifiers don't make the mistake I've implied above? I'm worried about the guy that comes after me. Maybe I should just ignore that and move on.