Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
I'm looking at a feeder that terminates in a 1200A MCB with a 80% rating for a 480V MCC. The E&C firm did not add 125% to the feeder ampacity as required by section 215.2(A)(1)(a). The MCC is considered a 'continuous load' but its lightly loaded. Is it possible to use a 'special permission scenario' by the AHJ per 90.2(C) to avoid rework if the calculated load shows the MCC will never go beyond 80% of its overall capacity?