In my line of work, I perform a lot of voltage drop calculations with a spreadsheet. In that spreadsheet I have a set value for K of 11.1. I see a lot of post using the same formula but 12.9 is stated for K, which I believe comes from NEC. As I look at various reference material such as ANSI/IEEE, Ugly’s, ASTM, equipment manufacture, etc I see values ranging from 10.7 to 13.1 for K of copper.
Since I am a data collection nut, I have measured numerous high current circuits, and reversed engineered the value of K and have found it ranges from 10.7 to 11.5. So I choose to use 11.1 as an average. DC currents are on the low end, and AC on the high end, naturally.
My question is why does the NEC use such a high number for K of copper? It seems to conservative, and would cause to oversize most of the time.