SPECIFICATION ON DEPTH OF TRENCH

Status
Not open for further replies.

DBLOCKER

Member
What is the specification for depth of trench for underground electric cable? This cable is going from the transformer to the building
(residential)
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: SPECIFICATION ON DEPTH OF TRENCH

the answer is - "it depends".

the answer is different for cable versus metal conduit versus plastic conduit.

it's different if you have to run under a driveway, or a slab.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: SPECIFICATION ON DEPTH OF TRENCH

Assuming this is not under a POCO's control, it would be covered in article 300.5.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: SPECIFICATION ON DEPTH OF TRENCH

Bob Peterson, see line 11 of this ERRATA

Roger
 

physis

Senior Member
Re: SPECIFICATION ON DEPTH OF TRENCH

11. Page 70-126

Table 300.5 Revise table as follows: In ?Column 4? and ?Column 5? change the SI unit value from ?50? to ?150 ? in the ?In trench below 50-mm (2 in.) thick concrete or equivalent? row.
Edit: I wonder why the choise to say SI unit instead of simply being obvious and saying 50 mm and 150 mm? :roll:

I know, I complain about this sort of thing too much.

[ July 27, 2005, 04:24 PM: Message edited by: physis ]
 