What’s your input voltage? What’s the output (boost or buck) voltage needed? If the input is 480, the second one could clearly not be used.
If you scroll down on the Hammond catalog you took this snip from, at the bottom of the column there is a connection diagram number, which will correspond to a connection diagram a few pages down. This will show the winding arrangement graphically so you can see the difference between the two.
I think that the two transformers have identical winding ratios, and so if you have <= 240V on the primary, you can use either transformer, and you'd wire it the same either way. So the only difference would be that the first transformer has higher voltage ratings on its windings.The first one has two 24v secondaries, while the second one has two 12v secondaries.
With the first one's secondaries in parallel, or the second one's secondaries in series, they're funtionally identical.
Thank you for your response.The first one has two 24v secondaries, while the second one has two 12v secondaries.
With the first one's secondaries in parallel, or the second one's secondaries in series, they're funtionally identical.
For the configuration you have used, either would suffice. Do you need a center tap?
Thanks for your reply.I think that the two transformers have identical winding ratios, and so if you have <= 240V on the primary, you can use either transformer, and you'd wire it the same either way. So the only difference would be that the first transformer has higher voltage ratings on its windings.
Cheers, Wayne
Technically yes, both transformers have a 10:1 ratio, but there are two sets of windings. You have to wire them differently based on your desired primary and secondary voltage. Looking at the second model (120X240 to 12X24) you can see that for a 100, 110, 115, or 120V low voltage, there are two different available voltages to boost to, depending on if you arrange the secondary windings in series or parallel. If there were simply two windings (one primary, one secondary) and the transformer is always wired the same way to boost, there would be no ability to have two different voltages to boost to.I think that the two transformers have identical winding ratios, and so if you have <= 240V on the primary, you can use either transformer, and you'd wire it the same either way.
I'm not seeing that you'd have to wire them differently, just that you'd have the option to wire the 240Vx480V unit differently. In the following I'll use a voltage of 240V, but you could use 200V and just multiply all the voltages by 5/6.3) To get the necessary 240V and 24V connections they would be wired differently.
So I think that each transformer can give you a 5% or 10% boost for the 200V input range, and only the 240Vx480V can give you a 20% boost.2) I think for the 200V input range the higher voltage version will give you options for up to a 20% boost, and the lower voltage version will give you options for a 5% boost. Both give you the desired 10% boost.
The voltage output would be the same, but you would hit the design current through the windings at only 50% of the rated kVA.For the first transformer, you could hook it up exactly the same, and it would behave the same.
The voltage output would be the same, but you would hit the design current through the windings at only 50% of the rated kVA.
Probably also a 110.3(B) issue.
Agreed that there are many configurations that are not at the 'rated' voltage, such as the 200 to 220V example above, where it is only 83% of the rated voltage (and hence the boost is only 20V, 83% of 24V). However, these configurations are approved for use by the manufacturer. Under each of these voltage configurations the manufacturer specifies how the transformer is to be wired - in this case it is connection diagram #1. If the manufacturer's instructions say to use connection diagram #1, and you use connection diagram #4, I think someone could make a case that you are not using the equipment "in accordance with any instructions included in the listing, labeling, or identification."AFAIK there is no prohibition or manufacturer instructions that prevent using the transformer below its rated voltage. In fact many intentional buck/boost configurations use the transformer coils at lower than their 'rated' voltage.
I would not be surprised that there is actually a low voltage limit where enough magnetizing current cannot be created, but it would have to be extremely low.But as we both noted doing so reduces the kVA capacity of the transformer.
Thank you for pointing that out, that was what I was missing.My reasoning was that using the 240x480 transformer with the primaries in series for the 200V application 'throws away' half the kVA capability,