You cannot just try to lower the voltage (assuming that's what the device was) without risking burning up the motor. But the problem is that this is a single phase motor, so there are very few possibilities available to you and if you can use anything at all, you have to know exactly WHICH type of single phase motor you have, there are several.
IF it is a Permanent Split Capacitor (PSC) type, then you can use what's called a Variable Frequency Drive that alters the voltage and frequency together, which avoids stressing the motor out. Tis is the only viable option open to you. If that can work, you need to use a VFD that is SPECIFICALLY designed to operate a SINGLEPHASE MOTOR. There are many many available to operate a 3 phase motor, and many that can operate a 3 phase motor from a single phase source, btu only a small number (2 or 3) that can operates a single phase MOTOR. Be careful about what you read.
If the motor is a Capacitor Start / Induction Run (CSIR) or Capacitor Start / Capacitor Run (CSCR) , or a Split Phase type, you cannot use speed control of any type without ruining the motor. Sorry. (I am assuming this is too big to have a Shaded Pole type single phase motor)
How to tell the difference? It's difficult without full motor details from the nameplate and/or manufacturer of the motor. Split Phase type will not have a capacitor "bump" in the side of the motor case, CSCR will have two bumps on the side. But there is no outside visible difference between a PSC and a CSIR type motor.