For
3 phase systems, it was (not in this order);
- Mechanical Vari-drive (variable pitch pulley) system
- Gear boxes
- Fluid couplings
- Particle clutches
- Eddy current clutch drives
- Cycloconverters
Versions that require a different TYPE of 3 phase motor:
- 2 speed motors (or 3 speed etc.)
- Wound Rotor Induction Motors
For the most part, prior to the modern VFD, changing the speed of the LOAD was not done with the motor, the motor was run at full speed and there was something else that changed the speed to the load.
"Dimmers" can only work on a select few types of SINGLE PHASE motors, like Shaded Pole and some PSC motors in specific applications like fans. If you only change the voltage to an induction motor, it just reduces the torque that the motor produces, the speed wants to remain the same because speed is based on frequency. So using a "dimmer" to reduce the voltage will possibly reduce the speed if the load remains the same by decreasing the torque of the motor, but in attempting to get back to speed, the motor may burn itself up.