The available torque will reduce by about 25%. Not a big deal if it is sufficient to drive the load.I have a inverter duty rated motor (480V, 40HP, 3600RPM, 60Hz).
Motor being driven via VFD. I want to increase speed to 75Hz.
I am guessing the HP will remain constant and the torque will vary.
Should I be concerned with bearing temps or anything else?
HP2= 78HP
I did some research on motor...and it is rated to run at 90Hz.
If you have a 40HP motor that the mfr says is good to 90Hz and a 40HP drive with a load of 38.5HP at 75Hz, you should be good to go. program the protection in the motor as a 40HP with the standard nameplate FLA. A 100A feeder should be fine, assuming you have the correct size conductors of course and that the VFD is OK with being protected by that large of a breaker (or has its own breaker or fuses with it).I hope this makes sense...this is a blower motor application...I am told that it has characteristics of a centrifugal pump and a positive displacement pump (curve is in between the two).
The vendor rep told the project manager that at 60Hz the motor should be seeing 21.8HP...and increasing to 75Hz will increase to 38.5HP.
I plan on taking amp measurements and verifying at 60Hz that we are drawing close to 30A. If this is the case, I will inform the PM that we can run motor at 75Hz safely.
Thanks for all the help.
I hope this makes sense...this is a blower motor application...I am told that it has characteristics of a centrifugal pump and a positive displacement pump (curve is in between the two).
The vendor rep told the project manager that at 60Hz the motor should be seeing 21.8HP...and increasing to 75Hz will increase to 38.5HP.
I plan on taking amp measurements and verifying at 60Hz that we are drawing close to 30A. If this is the case, I will inform the PM that we can run motor at 75Hz safely.
Thanks for all the help.
I'd guess probably a new "screw" blower like the Atlas Copco ZS, kind of a cross between a lobe type ("roots") PD blower and a screw compressor. I've seen them discussed but have never connected to one yet.I agree with Jraef. If the load is 38.5HP at 75 Hz, you should be OK.
I have just a minor niggle though........
All the fans and centrifugal pumps I have dealt with have been cube law loads. Applying that to your blower taking 21.8 HP at 60Hz equates to about 44HP.
That said, I don't know what kind of blower it is.
Could be, I agree.I'd guess probably a new "screw" blower like the Atlas Copco ZS, kind of a cross between a lobe type ("roots") PD blower and a screw compressor. I've seen them discussed but have never connected to one yet.