jmellc
Senior Member
- Location
- Durham, NC
- Occupation
- Facility Maintenance Tech. Licensed Electrician
I recently did a service call where a receptacle had burned up 2 different cell phone and battery chargers. Homeowner showed me where and arc had shot out and burned a mark on the floor. Everything I've seen before like that has been from a lost neutral. Old FPE panel, all I could find was a slightly loose main neutral lug; lug rubs a bit against the bar, not exactly a gap. I took apart and put a new lock washer in back , tightened again. Was better, still a tad of slipping. I asked power co to check their splices and transformers nearby. They said they found nothing. I saw no burn marks at the lug, not sure that was the only culprit but all I could find. Cases I've seen before happened from neutral/ground jumpers removed, loose neutral in panel or meter base, or loose neutral in transformer or service head splice.
It's been about 2 weeks; no further problems yet. Any similar experiences with any of you?