michalspike

Senior Member
On recent job I had the inspection and we use class 2 wire for 12V LEd strip light. We have remote drivers located in closet. we extend wires with class 2 wire using splicing it and tape exposed wire. Inspector came and fail us for it because he said it splice has to be in box. I tried to argue with him that I doesn't. Did I missed something ?
 
Terminations/splices for Class II circuits do not need boxes; 725.3.

On recent job I had the inspection and we use class 2 wire for 12V LEd strip light. We have remote drivers located in closet. we extend wires with class 2 wire using splicing it and tape exposed wire. Inspector came and fail us for it because he said it splice has to be in box. I tried to argue with him that I doesn't. Did I missed something ?

Did you extend the wires on the line side or supply side of the drivers?
 