Machiavelli999
Member
I am working on an installation of a tool that an AC Rack. It's basically a power distribution board. The AC Rack required a 300 amp feed, which I provided as 3 #350KCM & #4 GND.
When the tool arrived it had four lugs all sized for #350 KCM. The manufacturer admits their mistake, however we now have to deal with this.
The ground lug is too large to hold down the #4 GND conductor. The lug can hold down #1/0 AWG. Can I provide #1/0 from the ground lug to a nearby location where I would splice the #1/0 AWG conductor with the #4 GND conductor from the panelboard?
Looking through Article 250, 250.124 talks about Equipment Grounding Conductor Continuity, but it seems to only prohibit switching of the grounding conductor. Also, taps are permitted as discussed in 250.122(G). So, I do not see why this would not be allowed. It's obviously a sloppy solution, so if anyone has a more elegant way to solve this please let me know.
Thanks!
When the tool arrived it had four lugs all sized for #350 KCM. The manufacturer admits their mistake, however we now have to deal with this.
The ground lug is too large to hold down the #4 GND conductor. The lug can hold down #1/0 AWG. Can I provide #1/0 from the ground lug to a nearby location where I would splice the #1/0 AWG conductor with the #4 GND conductor from the panelboard?
Looking through Article 250, 250.124 talks about Equipment Grounding Conductor Continuity, but it seems to only prohibit switching of the grounding conductor. Also, taps are permitted as discussed in 250.122(G). So, I do not see why this would not be allowed. It's obviously a sloppy solution, so if anyone has a more elegant way to solve this please let me know.
Thanks!