We are installing a long run of 3" RSC in a Class 1 Division 1 location. We plan on pulling 3-250 MCM conductors through the conduit. There are many zigs and zags through the conduit run, which we handled by installing explosion proof LB after every 3 90 degree bends. Since the length of the cable is approximately 1500' we would like to install a splice in the cable in the classified area. Since the cost of an explosion proof junction box to meet wire bending requirements will present a time and financial burden, our thought is to use a 4" explosion proof "C" condulet with 4" to 3" explosion proof reducer bushings and use compression sleeves to splice the 250 MCM cables in the condulet. Does the NEC allow this? If this is allowed, are we required to place seal fitting at the condulet since the condulet is acting as a junction box and the conduit is larger than 2".
Thanks in advance,
Stu