solarken
NABCEP PVIP
- Location
- Hudson, OH, USA
- Occupation
- Solar Design and Installation Professional
I would like to understand if there is any 2023 NEC violation for using an insulated 600V Polaris 3-position tap connector installed in the wiring box of an Inverter to transition the 8AWG run from the array to two 10AWG conductors into two input terminals of the inverter. The tap would be located close to the terminals, with less than 12 inches of 10AWG. The Isc of the 2 strings combined that are feeding the 8AWG feeder is 21.16A,, and so the Imax is 1.25 x 21.16 = 26.45A, and the Ampacity required is 1.25 x 26.45 = 33.06A. I looked for busbar fingers with a lug compatible with the terminal blocks (like Midnite has) as an alternative and cannot find any.