To add, on either side of the Jbox above the trough, it denotes a single set of 3/0 in 2" conduit and 2 sets of 3/0 in 3" conduit. Not sure what is going on there.There are a few problems with this.
From FC-11 you have a 300 amp OCPD with one set of #3/0 so the wire is too small.
The tap to LP-1 has an EGC that's too small.
The parallel #3/0's are in a single raceway so it appears that they have applied derating to them but the EGC may not be the correct size.
No I think it's intended to mean 2-3" That's what 2 sets indicates.There are a few problems with this.
From FC-11 you have a 300 amp OCPD with one set of #3/0 so the wire is too small.
The tap to LP-1 has an EGC that's too small.
The parallel #3/0's are in a single raceway so it appears that they have applied derating to them but the EGC may not be the correct size.
They are coming out of FC-II with one set.Yeah there is something wrong here. My guess is that the 300 amp OCPD has only a single set of terminals so they couldn't parallel out of the FC-11. If they change the #3/0 to 350 kcmil it works.
No it clearly shows two sets of #3/0 in one 3" raceway. That's why there is only one EGC indicated, one raceway.No I think it's intended to mean 2-3" That's what 2 sets indicates.
Good catch. They obviously need a neutral for the panel LP-1.Sure hope they don't need 3 phase with a neutral.
There either running single phase with a neutral or three phase no neutral.
I bet if they feed trailers they need a neutral. Yet the panel is 3 phase 4 wire.
Nice to see what the feeder schedule says.
lots of questions there.
If they meant two conduits, it is usually indicated as 2 sets of 3 #3/0, 1 #3 g in 3" c ea. At least that's how I write them. This seems to indicate 1 conduit.No I think it's intended to mean 2-3" That's what 2 sets indicates.
Do not reduce the EGC size on a tap. 250.122(G). You size the EGC based on the OCPD for ahead of the tap.