Splice to Extend 4/0 and 2/0 feeder conductors

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
I need to extend some 4/0 line conductors and 2/0 neutral of an underground feeder about 6 feet. The conductors currently terminate on feed thru lugs of a meter-main outside, I will probably cut the conduit, pull the conductors out the bottom, and pull thru the wall inside to a junction box, and extend from there. Should I use a mechanical splice and heat shrink like this, or should I consider something else?
1731802427063.png
 
I need to extend some 4/0 line conductors and 2/0 neutral of an underground feeder about 6 feet. The conductors currently terminate on feed thru lugs of a meter-main outside, I will probably cut the conduit, pull the conductors out the bottom, and pull thru the wall inside to a junction box, and extend from there. Should I use a mechanical splice and heat shrink like this, or should I consider something else?
View attachment 2574409
I like those. What I like a bit better is the version that has two sets screws per side. A crimp would be best if you have the crimper for it. Personally I would put a layer of rubber tape then several layers of 88, them a heat shrink over it. Good for 100 years 👍
 