Just as conductors in raceways outdoors have to be identified as suitable for outdoor conditions (wet), so does all associated equipment, including splice blocks.If mounted outdoors, do the splices need to be made with an "outdoor rated" connector?
I am currently using Burndy/Polaris tap blocks, which come from the factory with anti-ox grease in each terminal. Would you consider this code compliant?
110.11 Deteriorating Agents. Unless identified for use in
the operating environment, no conductors or equipment
shall be located in damp or wet locations; where exposed to
gases, fumes, vapors, liquids, or other agents that have a
deteriorating effect on the conductors or equipment; or
where exposed to excessive temperatures.
Condensation in the attached raceways dripping in. Or just condensation on the walls of the enclosure itself.I do wonder why the interior of an enclosure that is rainproof would be considered wet.
Just as conductors in raceways outdoors have to be identified as suitable for outdoor conditions (wet), so does all associated equipment, including splice blocks.
However, I would say this requirement is often ignored regarding splicing and terminals in outdoor enclosures. :blink:
Just as conductors in raceways outdoors have to be identified as suitable for outdoor conditions (wet), so does all associated equipment, including splice blocks.However, I would say this requirement is often ignored regarding splicing and terminals in outdoor enclosures. :blink:
The interiors of raceways installed in wet locations may be considered wet locations by the NEC, but the interiors of enclosures installed in wet locations are not.
So the drain holes in a 3R enclsures are for?
Wouldn't these items be considered identified for use outdoors under the assembly listing... i.e. the panels or disconnects are listed for outdoor use and the breakers or fuses suitable for use within are part of the listing (though marketed and sold separately).Where do I buy outdoor identified breakers or fuses to use in 3R panels or disconnects?
Thanks for not picking on me... :lol:Not picking on smart here, it just seemed like the best post to quote for my question.
.... so does all associated equipment, including splice blocks.
I am aware of some of the test procedures. However, I'm not aware of any that establish the inside of a NEMA 3R rated enclosure installed outside as a dry location under the NEC.There are really only two choices when it comes to conductor insulation systems when installed in raceways Dry or Wet. It would not make any sense to refer to the inside of 'conduits' by any other descriptor.
One of the primary purposes of an enclosure is to 'provide a degree of protection' of the equipment inside the enclosure.
You may want to look into the 'test' criteria for different enclosure types.
I'm not aware of a requirement except as in 314.30 for handholes. Like iwire said, what about breakers, etc., where would this stop?If mounted outdoors, do the splices need to be made with an "outdoor rated" connector?
I am currently using Burndy/Polaris tap blocks, which come from the factory with anti-ox grease in each terminal. Would you consider this code compliant?
Thanks
So the drain holes in a 3R enclsures are for?
to drain the water out so it is not a wet area, just damp.