Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Splices in conduit bodies

In general there is not enough room in a conduit body to make splices in unless you use a conduit body larger than the raceway it is installed in.
 

redfish

Senior Member
Re: Splices in conduit bodies

Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code?
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">370.16(C)(2) 1999 NEC</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2002 NEC</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2005 NEC</font>