M moe314 Member Sep 10, 2005 #1 Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code?
Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code?
T torcho Member Location Wyoming Sep 10, 2005 #2 Re: Splices in conduit bodies Try 370-16(C)(2), it's legal as long as the LB is marked with a volume/capacity.
Re: Splices in conduit bodies Try 370-16(C)(2), it's legal as long as the LB is marked with a volume/capacity.
iwire Moderator Staff member Location Massachusetts Sep 10, 2005 #3 Re: Splices in conduit bodies In general there is not enough room in a conduit body to make splices in unless you use a conduit body larger than the raceway it is installed in.
Re: Splices in conduit bodies In general there is not enough room in a conduit body to make splices in unless you use a conduit body larger than the raceway it is installed in.
R redfish Senior Member Sep 10, 2005 #4 Re: Splices in conduit bodies Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code? Click to expand... </font> <font size="2" face="Verdana, Helvetica, sans-serif">370.16(C)(2) 1999 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif"></font> <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2002 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif"></font> <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2005 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif">
Re: Splices in conduit bodies Is it legal to make splices in conduit bodies such as "T"s and "LB"s and if not where can i find it in the code? Click to expand... </font> <font size="2" face="Verdana, Helvetica, sans-serif">370.16(C)(2) 1999 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif"></font> <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2002 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif"></font> <font size="2" face="Verdana, Helvetica, sans-serif">314.16(C)(2) 2005 NEC</font> <font size="2" face="Verdana, Helvetica, sans-serif">