Where does NEC say this is ok
Originally posted by sparkslord:
You can make splices in panels as long as you do not exceed the limits within 310.8.
Just for clarification.![]()
Not so fast, read the section carefully and see if it applies to conductors that are simply running from the cable or raceway connector to the OCPD.Originally posted by ryan_618:
Yes.
Well I do not see how it can apply to conductors that are not feeding through or tapping off to other switches or overcurrent devices,Originally posted by ryan_618:
I still don't see how it wouldn't apply, even after reading it.
They described the specific conductors for a reason, IMO if the section meant what you think it does all they would have to say is conductors.312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.