Re: Splices in panel
Guys, don't overlook the "unless adequate space for this purpose is provided" section of that sentence. As long as there is adequate space, even conductors that are "just passing through" may be so spliced.
This is done when adding a non-whole-house transfer switch to an existing service. We're not required to remove the home runs from the main panel. We ust route the utility current to the transfer switch and back.