NEC 2017... Is there anything in the CODE that talks about making multiple splices (480V circuits) in an enclosure to extend circuits? Does it have to be splices or can it be feed through terminal blocks rated for the application?
 
As long as you use connectors or terminals within their conductor range rating either one will work.
 