Splices

Status
Not open for further replies.

nathan1

Member
Im having a mental hiccup I cant find the article in the code that states that 120volt splices must be made in a junction box. Also in there is exposed romex in a kitchen cabinet above a range hood does this violate code. I dont like it a want to change it but I dont want to state it a code violation if it is not. Thanks in advance.
 
Re: Splices

300.15
(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice, junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways. The covers shall be accessible after installation.

334.10 (A) Type NM. Type NM cable shall be permitted as follows:
(1) For both exposed and concealed work in normally dry locations except as prohibited in 334.10(3).
 
Re: Splices

UL has listed NM splice connectors that are approved for use without a box, however the NEC does not permit it?

If a non-reversible, properly insulated splice is made at a point where no terminations or quipment is connected, why would a box be needed?

What is the code intent on this.
 
Re: Splices

Originally posted by bphgravity:
UL has listed NM splice connectors that are approved for use without a box, however the NEC does not permit it?
IMO 334.40(B) allows these connectors. :)
 
Re: Splices

I am not as familar with these fittings as I would like to be, but does the splice fitting cover the 'sheathing' as required in .40 "Openings in such devices shall from a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the coverings has been removed."

The splice devices I am aware of do not fit over the sheathing of the cable.

Pierre
 
Re: Splices

tap2.gif


ECN Thread on this
 
Re: Splices

Its been a while since ive been on this forum and i have to admit i havent seen this splice kits for romex. has anyone actually seen and used these and think its a good idea. I know they look handy but would you put one in your own home????? Im not trying to be sarcastic im just really curious. :confused:
 
Re: Splices

without assuming anything and not in a position to research books, I thought all splices were to remain accessible, no buried boxes. I will look it up later???

paul
 
Re: Splices

I recently worked on a couple bathrooms where the last electrician (or individual) used the wall as a junction box. This thing would be a definate improvement over that. And it sure looks like an easier way to correct it than what I had to do. I can't see needing these very often but occationally they could be pretty handy.
 
Re: Splices

Originally posted by pierre:
I am not as familar with these fittings as I would like to be, but does the splice fitting cover the 'sheathing'
Pierre
Yes, if they're installed correctly. These devices are commonly used in motorhomes and manufactured homes. I'm not positive, but I don't think they are approved for use in ordinary stick-built houses. The Molex SC Power Connector is one brand name of this type of connector.
 