Can you splice a short neutral in a panel so it will reach the terminal? If so does it have to be by hypress?
Yes you can splice it and no it does not have to be crimped.
of course it depends on what neutral you're talking about Service neutral or branch circuit and what size.
 
Yes you can splice it and no it does not have to be crimped.
of course it depends on what neutral you're talking about Service neutral or branch circuit and what size.
Could a service neutral be spliced with something like a polaris lug?
 
My understanding is you can splice any wire needed to add length in a panel as long as an appropriate splicing method is used. Be it a wire nut, crimp, Polaris, split bolt, etc….
The only caveat I can think of is no splicing of the GEC of the GES that isn’t an “irreversible” method. Am I wrong????
 
My understanding is you can splice any wire needed to add length in a panel as long as an appropriate splicing method is used. Be it a wire nut, crimp, Polaris, split bolt, etc….
The only caveat I can think of is no splicing of the GEC of the GES that isn’t an “irreversible” method. Am I wrong????
I've never understood the irreversible method for GEC but the acorn nuts connecting the ground wire to ground rods could be removed at any time if one would choose to do so.
 