Splicing alum water bond wire

Status
Not open for further replies.

bth0mas20

Senior Member
Location
Maryland
What is the best method to splice/extend a water bond wire that is aluminum?

Other than replacing the wire completely. At times when altering a service the wire is 1 ft too
short to reach.
 
Trevor was asking if it is a grounding electrode conductor because you cannot splice it unless you use an irreversible connector.
 
I use t&b c taps that are crimped on to the gec and the inspectors are good with that as long as its accessible. However these are not rated for use with aluminum...copper only.
 
That would work providing you have the proper crimping tool. If it's not the GEC you could use a split bolt.
 