Splicing & bonding in Metal Trough

Merry Christmas

pkelectrical

Member
Location
NJ
Here is the setup

300A generac disconnect service rated feed by 350 mcm ALU

1. (2) 200A subpanels in the basement & 200A fusible disconnect with 110A fuses for Steam unit
Running 250 mcm copper from the 300A disconnect and using 3/0 copper taps for the sub panels and 1/0 Alu tap for the Steam disconnect

Table 250.102(C)1 calls for #2 copper bonding. The 300A Generac has 1/0 Copper bonding jumper

Q1. Why does the 300A generac has 1/0 bonding jumper? Is it oversized or I need to run 1/0 bonding to the subpanels/trough/disconnect etc as well?
Q2. I noticed 3/0 SER Copper (not being used in this installation) has 1/0 ground as well. Is there a reason why they make it with 1/0 where smaller size would be sufficient?
Q3. Can I run for example 1/0 Bonding jumper from the 300A ATS and bond the trough and then run all my other bonding to it? Or I have to run the back to the ATS? (what I would normally do, but that is 50' run)
In my opinion if I ran 1/0 Copper bonding from the ATS to the trough and run the other bonding to it, it would be a better system then running #2 Copper bonding jumper from the ATS and then loop bond all the equipment

What are your thoughts?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The first thing that comes to mind is the 350AL is undersized for a 300 amp service rated T/S.
Generac may have installed a 1/0 bonding jumper to cover the possibility of someone installing a conductor larger than 350AL
Anything on the load side of the 300 amp ATS will only require a #4 Cu or #2 AL bond/equipment ground.
 

pkelectrical

Member
Location
NJ
The first thing that comes to mind is the 350AL is undersized for a 300 amp service rated T/S.
Generac may have installed a 1/0 bonding jumper to cover the possibility of someone installing a conductor larger than 350AL
Anything on the load side of the 300 amp ATS will only require a #4 Cu or #2 AL bond/equipment ground.
350 mcm works for 300 A. 75 degree column rated at 250A/.83= 301A
Per 250.102(C)1 over 3/0 through 350 requires #2 copper or 1/0 Alu
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You are correct.. I forgot the .83 residential... too accustomed to commercial.
On the LOAD side of the 30 amp breaker Table 250.122 would apply, not 250.102(C).
 