Is it permissible to splice the GEC from the service disconnect to the water supply line? Furthermore, does it matter where the GEC attaches to the water supply line provided that there is a bonding jumper accoss the meter?
I do understand that the GEC to ground rod can not be spliced.
Thanks
Yes, if done properly 250.62(C)
The way I read it, yes. 250.52(A)(1) states that beyond 5 ft the line shall not be used as a grounding electrode conductor.
Thanks
misunderstand...see 250.62(C) again
Gus, Sorry to interrupt, but did you mean [250.64(C)]? rbj
interruptions welcomed.... eyeglasses more welcomed.... thanksView attachment 3855
250.64
(some times I fail to see the top of the page evidently)