Under NEC 392.8a, do you think that wire nuts are considered an approved splicing and insulating method for 12awg wire carrying 120vac in a cable tray?
Thanks
2008
Under NEC 392.8a, do you think that wire nuts are considered an approved splicing and insulating method for 12awg wire carrying 120vac in a cable tray?
Thanks
Are #12 single conductors allowed in cable tray?
392.10(B)(1)
(1) Single-conductor cables shall be permitted to be installed in
accordance with (B)(1)(a) through (B)(1)(c).
(a) Single-conductor cable shall be 1/0 AWG or larger and
shall be of a type listed and marked on the surface for use in
cable trays. Where 1/0 AWG through 4/0 AWG single-conductor
cables are installed in ladder cable tray, the maximum allowable
rung spacing for the ladder cable tray shall be 225 mm (9 in.).