123ozzie
Member
- Location
- chicago illinois
Good morning, I know that per 314.16(c)(2) splicing is allowed in conduit bodies, just need to clear up how many are allowed. I have an Appleton LB that, including the cover, is good for 8.8 cubic in. (Appleton website). I have a hot #12, neutral #12, and a ground #12 spliced in the LB. According to table 314.16(B) each #12 is calculated as 2.25 cubic in. Am I right in thinking that I have 2.25x6=13.5 cubic in. of wire splicing in the LB? If so I would be over by 13.5-8.8=4.7 cubic in. Do "current carrying conductors" come into play? Thanks in advance for any response.