If you splice ccc's in a conduit body do you have to use a bonding jumper?
If you splice and egc (and only the egc) in a conduit body do you have to use a bonding jumper?
250.148 only addresses boxes and I can find nothing related to conduit bodies beyond not exceeding fill when splicing.
If you splice and egc (and only the egc) in a conduit body do you have to use a bonding jumper?
250.148 only addresses boxes and I can find nothing related to conduit bodies beyond not exceeding fill when splicing.