We are performing work for a NYC government agency. We are running 4#12 and 2#12 grounds (2 - 277 volt ckts. with 2 grounds) in 3/4" conduit for lighting. At each fixture, we need to splice onto one of the circuits. So the calculation for each splice point:
2 wire pass thru = 2 #12.
2 coming in, 2 going out, 2 to fixture = 6#12.
1 grounding = 1 #12.
total 9 #12 @ 2.25 cu. in. = 20.25 cu. in. required.
We proposed a 1" mogul condulet that has 31 cu. in. space.
We also noted that we would support the conduit within 12" on both sides of the condulet.
We submitted this and showed these calculations.
The comment came back "a dedicated code-size splice box for each lighting fixture shall be provided."
By code, is there anything wrong with what we submitted? By industry standards is there anything wrong with this?