You could probably do it with a steel LB. You will probably have to hammer them back in to get the cover on and that will probably break the body.
Also they are not listed for splices.
Have three #2 and one #4 AL XHHW conductors coming into 2 inch PVC LB and four of the same going out. The LB is rated at 63 C.I. The distance between the 2 entrances is less than the six times the pipe size. Can I splice in this LB?
The point would be moot anyway, the volume allowance is only for conductors # 6 awg and smaller.Did you calculate the fill to see if the LB is large enough? If not the point is moot.
Rick
314.16(C) Conduit Bodies.
(1) General. Conduit bodies enclosing 6 AWG conductors or smaller, other than short-radius conduit bodies as described in 314.5, shall have a cross-sectional area not less than twice the cross-sectional area of the largest conduit or tubing to which they can be attached. The maximum number of conductors permitted shall be the maximum number permitted by Table 1 of Chapter 9 for the conduit or tubing to which it is attached.
(2) With Splices, Taps, or Devices. Only those conduit bodies that are durably and legibly marked by the manufacturer with their volume shall be permitted to contain splices, taps, or devices. The maximum number of conductors shall be calculated in accordance with 314.16(B). Conduit bodies shall be supported in a rigid and secure manner.
Its in the quote you posted. "shall be calculated in accordance with 314.16(B)". Table 314.16 only lists conductors up to # 6 awg.
Rick
Why the limitation to 6AWG on this rule? Is there a separate rule for area in the conduit body for wires over 6?