Z zapped 1 Member Location north port fl Mar 26, 2012 #1 i have read 314.16 c 2 does that mean its ok to splice in lb as long as it has cubic inches marked
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 26, 2012 #2 Its o.k, if the conduit body has the volume maked and you don't exceed that number using 314.16(B)