W wyboy Senior Member Sep 30, 2010 #1 Can low voltage light wires (12 volt) be spliced behind sheet rock or not in a box?
raider1 Senior Member Staff member Location Logan, Utah Sep 30, 2010 #2 Class 2 and 3 circuits are not required to meet the requirements of Chapter 3 unless specifically reference in Article 725. So short answer, if you are using a Class 2 or 3 wiring method you are not required to splice the conductors in a box. Chris
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 1, 2010 #3 Just be careful using the term low voltage. To a utility lineman, 480 volt street lighting is low voltage. The NEC does not define low voltage.