In a repair, I need another inch. Is it generally acceptable to use a connector to lengthen a 4/0 AL neutral wire in a residential panel? I've never done that but have seen it sometimes. thank you
 
In a repair, I need another inch. Is it generally acceptable to use a connector to lengthen a 4/0 AL neutral wire in a residential panel? I've never done that but have seen it sometimes. thank you

230-46 allows it for service conductors
 